250.32 Buildings or Structures Supplied by a Feeder(s) or Branch Circuit(s).
Exception: For installations made in compliance with previous editions of this Code that permitted such connection, the grounded conductor run with the supply to the building or structure shall be permitted to serve as the ground-fault return path if all of the following requirements continue to be met:
- An equipment grounding conductor is not run with the supply to the building or structure.
- There are no continuous metallic paths bonded to the grounding system in each building or structure involved.
- Ground-fault protection of equipment has not been installed on the supply side of the feeder{s).
If the grounded conductor is used for grounding in accordance with the provision of this exception, the size of the grounded conductor shall not be smaller than the larger of either of the following:
- That required by 220.61
- That required by 250.122