Bob
To borrow from Charlie, what I posted was not what I was trying to say, and what I was trying to say is not what I posted.
I will try again and try to do a little better.
300.5(D)(5) was moved to 300.5(B) in the ?05 cycle and addresses cables and conductors installed underground. This requirement states that any conductor or cable that is to be installed underground
must be listed for a wet location. It does not give me the rules for each cable or conductor. These rules I will find in the cable or conductor article.
Now I go to the
SE Cable Article to see if the
Cable is listed for wet location and what do I find in 338?
I find two difinations that describes SE cables. One states that it is identified for underground use and the
cable to use for under ground installations.
338.2 Definitions
Service-Entrance Cable. A single conductor or multiconductor assembly provided with or without an overall covering, primarily used for services, and of the following types:
Type SE. Service-entrance cable having a flame-retardant, moisture-resistant covering.
Type USE. Service-entrance cable, identified for underground use, having a moisture-resistant covering, but not required to have a flame-retardant covering.
This section of code directly addresses the use of SE cables for underground use and overrides the general term used in 300.5(B). Notice that the definition of USE does not state direct burial, it only address the use of the cable for underground installations.
When I addressed 340 I was trying to show that there was a Article that addressed a cable that is to be used as a branch circuit or feeder. One could install MC cable as long as it complied with 330.10(A)(5).
What I was addressing was the use of SE-R installed in a raceway and buried. Unless this SE-R cable is identified for underground use then it is in violation of 338.
Using the train of thought that you have expressed in this thread could be a little misleading. For example, could I install NM-B in flex on the outside of a dwelling unit for the AC unit?
Using your thinking that the conductors in SE-R cable are THW conductors would be the same as me saying that the conductors in NM-B is dual rated at THHN/THWN.
The SE-R cable would need to be listed for underground installation no matter what kind of conductors are in it.
I hope that my post is now a little more in line with what I was trying to say.