I am currently attending a class at a local community college. The subject is Master Review, to take the Master Lisence test. The question was brought up about box fill calculations. In 314.16 (4) counting the conductors on a device. If you have two devices in a box, say (1) one Receptacle with 2-#12's and (1) one switch with 2-#14's. How are the yokes of each device counted? Some say the yokes count as double volume allowance of the largest conductor in the box. Some say double volume allowance for the largest conuctor on each individual device. The switch is the device in question.
The switch's yoke counts as:
A) 2-#12's
B) 2-#14's
Which is correct? Was it originally the largest conductor in the box and was a code change? Our instructor is unsure of the terminology in the code.
Can Someone help us?
Thank you,
kgasparky
Have you read 314.16(4)?
When I read it I see it says, more or less the following
....based on the largest conductor connected to the strap...
B) - 2 #14's
314.16(B)(4) ~ Device or Equipment Fill.
For each yoke or strap containing one or more devices or equipment, a double volume allowance in accordance with Table 314.16(B) shall be made for each yoke or strap based on the largest conductor connected to a device(s) or equipment supported by that yoke or strap.
The conductor attached TO the device is the one that is counted...hower, if there are clamps, they are sized accoring to the largest conductor entering the box...and if there are equipment grounding conductor or equipment bonding jumper, they are sized to the largest EGC/EBJ present in the box.
Jim W in Tampa said:
see 314-16
You got some 'splainin' to do!
BTW, THIS is my 200th post
That was nice to send the guy your picture but whats with the birthday thing, he never mentioned that.
Ok..beat me up guys....2000 th post
LOL
See what happens when you work past dinner time two nights in row.