billdozier
Senior Member
- Location
- gulf coast
Hey guys boss asked me to size wire and pipe for a 225a mb singlephase subpanel. Just want to make sure I did this correctly as I havent done much of this. Started at 310.15 ampacity table. Found xhhw wire which would be 200mcm alum I then went to index where you have conduit fill Found the schd 80pvc calc called for 4 200s in a 2 and 1/2 pipe. Then went to 250 equipment grounding table and ordered a #4 al ground if I remember correctly. We chose not to downsize the neutral. Could we have downsized the neutral? what code reference for the correct size neutral if downsized? Thanks for your help