ptonsparky
Tom
- Occupation
- EC - retired
Sounds like it is ungrounded to me. XFMR case to earth does not make it a grounded system. Typically XO needs to be earthed, or whatever serves as your "earth" and connected to the bare ground wires at a single point after which they are isolated from each other.Here are my readings from the first main panel:
L1-L2 = 202v
L1-L3 = 202v
L2-L3 = 202v
L1-N = 117v
L2-N = 117v
L3-N = 117v
L1-GND = 151v
L2-GND = 250v
L3-GND = 96v
N-GND = 136v
The XFMR is grounded to earth, along with the bare ground wires from both the Primary and Secondary feeds. Does this sound like an ungrounded system? The xmfr is primarily used for lighting and feeds several subpanels from the main panel.