different voltages

Status
Not open for further replies.

j rae

Senior Member
Can you run both 277v and 120v circuts in the same conduit> Can they be in the same j-box?? Which article in code?
 
Start with 200.2(D) which tells you how to identify the grounded conductors when different systems are in the same raceway or enclosure and then go to 300.3(C)(1) which gives further explanation.
 
haskindm said:
At least Raider and I are on the same page, he just types faster!

Well thats a first, usually I am the slow typer.:D

And you did provide a reference to 200.2(D) that I didn't.

Chris
 
Don't forget about the rule in 210.5(C) and that applies even when the conductors are not in the same raceway or enclosure.
 
Status
Not open for further replies.
Top