Re: dimmers
Originally posted by al hildenbrand:
Originally posted by rick hart:
OK let's REALLY go over the deep end:
How much power is being consumed when the 100% lamp DIMMER is at full?
100 W ? 120 V = 0.8 A
The power dissipated at the triac heat sink in the dimmer, running the bulb at 99% will be just slightly less than:
0.8 A ? 0.7 V = 0.56 Watt
.
i would agree with al hildenbrand interms of power loss at dimmer.
But not in total power consumption...
As far as dimmer concern, it may (?) consume 0.56w whether it is low mode or high mode,irrespetive of regulation.It is constant once you turn on the Dimmer.
But as far as load concern (any kind of load),
the resistance remain same ,we are not controlling the resistance of the load here....
Forget about diac,triac,thyrister etc,.See the fundamental........
If ,we assume the dimmer is controlling the voltage here.the load (100w) will consume more current to meet the power demand of the 100w bulb,since the resistance remain same.
(Second one,It is just for a debate) If we assume the dimmer is controlling the current, the load (100w) would consume more voltage to meet the 100w power demand,since the resistance remain same.(But practically it is not possible because our system has standard voltage of 120V)
So, as far as my concern,once the dimmer is turned on, the entire system (100w load + Dimmer) will consume 100W+0.56W= 100.56W.
I really dont konw what exact power consumption,that may includes wire loss also.
So let us wait till
MARIO go to site and come back with clear picture.
Thanks for all...
Jeyakumar