Dimming high bay LED lights not using low voltage

Customer wants 23' high new gym LED lights dimmable. The ones I am viewing are dimmable 0-10 volt. But the existing 20 yr old fluorescent lights probably don't have low voltage wiring ran. Are LED high bay lights available in 120 volt dimming ? Thank you
 

hillbilly1

Senior Member
Location
Atlanta,Ga
Occupation
Field coordinator/ technical support
You should be able to get wireless 0-10 volt dimming modules if running a low volt cable would be difficult.
 

DrSparks

The Everlasting Know-it-all!
Location
Madison, WI, USA
Occupation
Master Electrician and General Contractor
Just run 18-2 thermostat wire to each fixture. You can daisy chain them. I do it all the time.

Sent from my BE2028 using Tapatalk
 

jedoll

Member
Location
California
Occupation
Engineer
You should be able to get wireless 0-10 volt dimming modules if running a low volt cable would be difficult.
Better than wireless is a 0-10V Blink'n'Dim Adapter. It enables dimming control from any existing switch. Works with networked switches too. No batteries, RF interference or distance limits. About $70 on Amazon.
 