Dimming high bay LED lights not using low voltage

Status
Not open for further replies.

Stevenfyeager

Senior Member
Location
United States, Indiana
Occupation
electrical contractor
Customer wants 23' high new gym LED lights dimmable. The ones I am viewing are dimmable 0-10 volt. But the existing 20 yr old fluorescent lights probably don't have low voltage wiring ran. Are LED high bay lights available in 120 volt dimming ? Thank you
 

DrSparks

The Everlasting Know-it-all!
Location
Madison, WI, USA
Occupation
Master Electrician and General Contractor
Just run 18-2 thermostat wire to each fixture. You can daisy chain them. I do it all the time.