Do dwelling unit dining room receptacles have to be on 20 ampere branch circuits?
Please read carefully the second to last sentence of 210.52(B)(3), which reads: "Additional small appliance branch circuits shall be permitted to supply receptacle outlets in the kitchen and other rooms specified in 210.52(B)(1)." I cannot find any place which states that small appliance branch circuits have to be 20 ampere. (I understand that there have to be at least two (2) 20 ampere branch circuits, and have those.) Note that 210.11(C)(1) refers to 210.52(B), which includes the sentence referenced above.
I take the sentence above to mean that I can have additional small appliance branch circuit(s) to serve the dining room, and, lacking anything to the contrary, they can be 15 ampere. No?
Please read carefully the second to last sentence of 210.52(B)(3), which reads: "Additional small appliance branch circuits shall be permitted to supply receptacle outlets in the kitchen and other rooms specified in 210.52(B)(1)." I cannot find any place which states that small appliance branch circuits have to be 20 ampere. (I understand that there have to be at least two (2) 20 ampere branch circuits, and have those.) Note that 210.11(C)(1) refers to 210.52(B), which includes the sentence referenced above.