Re: Dining Room Receptacles
Tony I do not know what else we can show you, maybe ask a few inspectors in your area if they except 15 amp circuits for kitchens and dinning room outlets.
The requirement for kitchen GFCIs is "where the receptacles are installed to serve the counter top surfaces"
A floor standing refrigerator with an outlet behind it will not need a GFCI protected outlet.
The only purpose of Exception 2 is to allow a single 15 amp outlet (not a duplex) to serve a refrigerator