Is 2-2-2-4 made or common for direct burial? It's a greenhouse, 60 amps. My supply house thought it was a special order. I will probably do conduit but of course the owner wants cheap as possible.
Why #2 for a 60A feeder? Voltage drop?
If not and the load is 55A or less you could use #6 4W UF.
2-2-4-6 mobile home feeder is so common it is usually cheaper. I use it all the time even if I don't need ninety amps worth of wire.Why #2 for a 60A feeder? Voltage drop?
If not and the load is 55A or less you could use #6 4W UF.
Chances are, that UF copper is more costly!!
2-2-4-6 mobile home feeder is so common it is usually cheaper. I use it all the time even if I don't need ninety amps worth of wire.
Okay, I did not know that. Cool.