- New Jersey
- Journeyman Electrician
Ahh. I took your post to do more with the installation methods and such. My bad.
No problem. My wordsmanship is somewhat lacking today.
That would be impossible, because they are not, in fact, emergency loads. Putting the ice cream freezer on an emergency ATS does not magically transform it into an emergency load. It has to be an emergency load, by definition, before you draw the one-line.
What world are you from?
An "ice cream freezer" is an "Emergency" need!!!![]()
So we pretty much are in agreement that a 2nd ATS is needed for the emergency/egress lighting.
So going back to the question... what do I do? Design it with a known code violation or go back to the builder and say no way I cannot do it as the building inspector is suggesting?
It seems I go with the second route.
Thanks for all the help.
Maybe it is. In the case of a power outage you gotta have your ice cream!That would be impossible, because they are not, in fact, emergency loads. Putting the ice cream freezer on an emergency ATS does not magically transform it into an emergency load. It has to be an emergency load, by definition, before you draw the one-line.
You know the right thing to do. Have you talked with the inspector to be sure they realize that the lighting doesn't have internal batteries? It is possible they don't understand.So we pretty much are in agreement that a 2nd ATS is needed for the emergency/egress lighting.
Especially at a plant that makes ice creamWhat world are you from?
At the end of the day your code complaint design is what customer is paying for.
In MA you need a separate ATS for life safety, and the life safety equipment must be located in its own 2hr fire rated room.
I don't fully understand the issue. Is the inspector saying you simply don't need a 2nd ATS or is he saying using a 2nd ATS is a violation?So we pretty much are in agreement that a 2nd ATS is needed for the emergency/egress lighting.
The inspector is saying you don't need the 2nd ATS for Emergency Lights.
Clearly that's a code violation and I decided I am willing to lose the client and just do the design per code.
So you want to install two ATS units per your code interpretation but the inspector says it's not required and the customer doesn't want two switches siding with the inspector?
Otherwise if the customer is OK with the added expense of two ATS's what's the problem? The inspector doesn't seem to be saying you can't do it, he just doesn't think it's required?
I agree with Andy's comment above. I don't see the issue with going above and beyond what the inspector is looking for. In this case "above and beyond" is simply code compliant but who is he/she to tell you that you can't over design something? Inspector is definitely wrong here but like I said, if you want want two ATS why can't you use two ATS if everything is code compliant?