I have a situation where I did the electrical design for an apt. bldg. with a generator.
The owner is putting in a generator large enough to power the entire building so the main house panel is going to be on the generator.
My design has a separate transfer switch / panel for the emergency/egress lights since they are considered life safety and the main house panel on the generator has other loads which can't be considered emergency.
The inspector said you don't need the second transfer switch and I am sure this is wrong. Obv. I know it will work but do I submit the design without the 2nd transfer switch (even though I know this is wrong) or lose a client/give back his money?
Thank You
I know I am very late to this game and many of you may not even see my response - the first clarification needed is to understand if this building will have utility power. You MUST establish "normal" power and "emergency" power sources. If there is utility power, that would be the "normal" source. Next question is what will the inhabitants of the building do when "normal" power fails - if they evacuate the building using genset-powered lights, then the genset is an "emergency" power source ... if, on the other hand, they continue to carry on life as normal, then the genset is simply a second "normal" power source. If they continue to occupy the building on genset power and there is no other emergency power source for egress lighting, how will they exit the building when the genset runs out of fuel, fails due to overtemperature or low oil pressure or for any other reason? If there is no utility power, then the genset is the "normal" power source and cannot also act as the "emergency" source. In this situation, if the genset fails, ALL lighting is lost.
If the intention is to continue occupancy on genset power, then the genset is a standby (second "normal" source) and there is no requirement for separate wiring systems, second ATS or any of the other stuff that goes along with EMERGENCY GENERATORS. There is, however, a requirement for battery-backup egress lighting so that the occupants can safely exit the building when / if the genset stops operating and utility power is still unavailable.
Although it is not written anywhere that I can find, it seems that emergency lighting (unit battery pack equipment) defines the intention that a building will be vacated within 90 minutes after "normal" power failure. If there is utility power and 100% genset backup but occupancy is intended to continue for more than 90 minutes after the genset starts, I put in battery E-lights. Maybe this is overkill, but I don't want the lawsuits when someone can't find their way out of a dark building.