Disconnect before service meter

DilipN

New User
Location
33613
Occupation
Engineer
We have disconnect switch after Service meter of 480 V service. Is additional disconnect is required before service meter? as per NEC230.71(C)
 
Disconnects ahead of the meter may or may not be a POCO requirement in your area. They are not required by the NEC
 
We have disconnect switch after Service meter of 480 V service. Is additional disconnect is required before service meter? as per NEC230.71(C)
Is the disconnect before or after the meter? A meter disconnect is permitted by the NEC but not required. As stated the service disconnect rules are unchanged whether there is a meter disconnect or not.
 