Disconnect height for Heat Pumps

Status
Not open for further replies.

jph320

Member
Location
Cinnaminson nj
Occupation
Electrician
I thought the max height for disconnects are 6'7? We have some heat pumps at work that you need a pole to reach the disconnect to shut it down.
 
Check the exceptions in 404.8 and see if any ares applicable.
 
% %

Would Exception # 3 be applicable for **jph320**?

% %
Per '08 Code:
I think exception 2 would be the most likely depending on the equipment location.
I doubt the switch he has would qualify as a "Switch-isolation" per NEC definition.
 