TwoBlocked
- Bradford County, PA
- Industrial Electrician
Yep...
Use an overlapping control contact at the disconnect to ensure the drive run command is off before the power is interrupted.
Yep...
Can you share your calculations?After the 1st time we ran a bunch of calculations and made sure wire sizing/distance/etc was all good.
What is the fan motor namplate rated voltage / HP.
Branch circuit size / breaker size?
You mentioned the wire is copper what is the wire size?
You mentioned the fan is 15 feet away from the disconnect.
How long is the run to the disconnect?
You mentioned you monitored the voltage was that on each phase L-L?
Light up the target a little bit with one of those little rechargeable work lights. If it's too bright smear something on the lens.Do away with the reducers and put in 110 amp fuses.
rk
What is/are the actual loads? Types.
Single, three phase? Mixed loads?
I have no idea what an indoor shooting range requires. My outdoor is a 1/2 mile and requires daylight.
I think I'd want to record current on all 3 phases for a few days and then look for something that deviates from the norm. Probably want to do voltage too.C phase is bottlenecked somewhere. If it killed a 200A DC something else is wrong.
Like tons of reactive power? Yeah put a scope on it.I think I'd want to record current on all 3 phases for a few days and then look for something that deviates from the norm. Probably want to do voltage too.
I wonder if there is anything in the circuit like line reactors or PF caps? Or if it's supplying something something with lots of rectification
The output of the VFD won't change.Out of Curiosity I would swap the phases and see if another phase burns up the same way. I believe the VFD can be programmed to correct rotation. If not just swap both line and load phases to correct rotation.
I know this is a simple approach but I would want to see if it happens to another phase.
Read HVAC tech story recently, guy determined gas valve was bad. Unit was rather old and he talked client into replacing the furnace. New furnace wouldn't fire after it was ready for run. Found out the gas company had disconnected service. You would think they would have figured that out before determining old unit had a bad gas valve?I've flown a over 1000 miles to go put eyes and hands on mysterious problems like this, and most times it's somebody doing something stupid and whatever I'm being told on the phone seems to be something from an alternate reality
Kind of worse yet, I had a builder change one my temporary 5-15 GFCI receptacles to be supplied by 240 volts.Back when I was a kid, we moved into a new house. First thing my dad did was put a window AC in. Thing made noise but didn't work.
Replaced the AC. Thing made noise but didn't work.
The 6-15 receptacle had been wired 120V. Whoops.
swap the phases twice so the fan doesn't loose its proper rotation, it'll happen again but at least you'll know if is the wire or the fan itself.Good afternoon all,
I have a situation that is stumping me.
My coworker installed a disconnect (100A 3ph 208v) for a client and the disconnect had the C leg melt, without blowing the fuse. So we replaced it, it happened again. Replaced it for a 3rd disconnect, and this time upsized the disconnect to a 200A heavy duty disconnect, and used fuse reducers to put new 100A fuses in.
Lo and behold, it lasted longer than the others, but ALSO melted the C leg without tripping the fuse... it took a couple of years to do so, but still ended up with the same result.
After the 1st time we ran a bunch of calculations and made sure wire sizing/distance/etc was all good. After the 2nd time we hired an outside engineering team to come in and do some studies, they deemed everything was fine. We have monitored it ourselves and keep coming up with the equipment pulling about 68A per leg...so not enough to trip the fuses, but somehow still melting the disconnect.
We assumed weak internal connections in the disconnect itself (faulty from the factory), but at this point after three disconnects met the same end, my coworker and I are a bit dumbfounded.
Anyone have any thoughts?
Thanks in advance!