Disconnect OCPD

Status
Not open for further replies.

The electron man

Senior Member
Location
Nyc
Occupation
Electrician
When I'm installing a disconnect do I always need a ocpd like a break or fuse in the disconnect ? or as long as I'm feeding from a breaker I can use a non fusible disconnect ?
 
And you also have to be aware of the interrupting current rating is of the disconnect. Example a non fused disconnect is rated at 10,000 AIC
 
Actually for any ocpd or disconnect the AIC rating must be considered. Typical resi installations are often 5,000 amps available at the transformer
 
So let's say I have a 60a disconnect, I have to make sure I don't run more then 60A through it ?
This came up in another thread but it wasn't the main topic. The company I was with at the time got documentation from a switch manufacturer (Eaton, Square D; I don't remember) that told us that their unfused safety switches must be protected by OCPD that does not exceed the rating of the switch. So, according to that documentation, yes.
 
But you me
How come I see ac disconnects with a breaker or fuse if its protected upstream
To quote Pat Paulsen (political comedian from the 60's), "The answer to that question is absolutely, without a doubt, 'who knows?'"
 
Some equipment is listed to have fuse protection (only) so, if you have a breaker panel, you must install fuses somewhere in the system to meet requirements.
So is it best practice to install a disconnect with a ocpd if I'm not sure about the equipment requirements ?
 