I am trying to get to the bottom of a discussion about the proper fused disconnect size that is needed for a chiller.
The MCA is 316.3 amps with an MOCP of 400 amps. The unit has 2 compressors with RLA of 119 amps each and 8 condenser fans with RLA of 5.4 amps each.
Total RLA is 281.2 amps. If I understand correctly, minimum disconnect size shall be not less than 115% of RLA which would be 323.38 amps.
I would think that a 400 amp disconnect would suffice but I have heard that a fused disconnect can only be utilized up to 80% of its rating for continuous loads. Is that correct?
Can I use a 400 amp fused disconnect in this application or do I need a 600 amp disconnect?
Also, I have a question about the MCA. Compressor 1 = 119 amps. Compressor 2 = 119 amps. 8 condenser fans = 43.2 amps total. I would think I calculate it as such. Largest load times 1.25 plus all other loads.
119 x 1.25 = 148.75
148.75 + 119 + 43.2 = 310.95
How was the 316.3 amp MCA determined?
Thanks!
The MCA is 316.3 amps with an MOCP of 400 amps. The unit has 2 compressors with RLA of 119 amps each and 8 condenser fans with RLA of 5.4 amps each.
Total RLA is 281.2 amps. If I understand correctly, minimum disconnect size shall be not less than 115% of RLA which would be 323.38 amps.
I would think that a 400 amp disconnect would suffice but I have heard that a fused disconnect can only be utilized up to 80% of its rating for continuous loads. Is that correct?
Can I use a 400 amp fused disconnect in this application or do I need a 600 amp disconnect?
Also, I have a question about the MCA. Compressor 1 = 119 amps. Compressor 2 = 119 amps. 8 condenser fans = 43.2 amps total. I would think I calculate it as such. Largest load times 1.25 plus all other loads.
119 x 1.25 = 148.75
148.75 + 119 + 43.2 = 310.95
How was the 316.3 amp MCA determined?
Thanks!