Don't do a lot of work on large rooftop or other completely self contained units, but can't recall ever seeing data on nameplate for a crankcase heater, and don't see too much need for it to be there, they shouldn't need to run while the compressor is running.
5 amps of control power added to the supply volts is 1200 VA @ 240 volts 2400 @ 480 volts. That is a lot of contactor coils, I think if it is that high it probably includes things like damper motors, or motorized zone valves or something of that nature.