I just took a look at a chiller with an optional wye/delta starter installed. Single compressor machine.
RLA: 283.3 amps
LRA: 578 amps wye/1800 amps delta
MCA: 354.1 amps
MOCP: 600 amps
MCA is RLA times 1.25 (283.3 x 1.25 = 354.125). MOCP is RLA times 2.25 then next size down (283.3 x 2.25 = 637.425). Next standard size down is 600 amps.
MOCP is the same whether starting across the line or wye/delta. It appears that MOCP is determined from RLA regardless of starting method/motor control. I'm pretty sure this is how it's done whether ATL, Y/D, VFD, etc. At least this is how it is with a listed unit. Outside of a listed unit, if I understand correctly, going by art 430, with a standard motor circuit, you can go higher than 225% with MOCP to permit starting if needed, correct? Forgive me, I've been in the HVAC world in a testing lab for a long time and I'm just trying to get a better understanding of the code.