texie
- Fort Collins, Colorado
- Electrician, Contractor, Inspector
225.33 is still the same in the 2020. 6 breakers in a MLO panel are fine.
You are correct, I was thinking I had heard it was changed to be inline with 230.71225.33 is still the same in the 2020. 6 breakers in a MLO panel are fine.
I see no good reason for that. With services you often have no readily available way to kill the supply conductors and will need to involve the utility if you want to kill the supply.You are correct, I was thinking I had heard it was changed to be inline with 230.71
Roger
You've never worked on a large university campus have you?I see no good reason for that. With services you often have no readily available way to kill the supply conductors and will need to involve the utility if you want to kill the supply.
With a separate building supplied by a feeder you do have ability to shut the feeder off. Still makes sense to have no more than six mains at the building though.
I was saying I hope they don't change it because I don't think it is a good idea. But won't be surprised if they eventually do change it. They like to change a lot of things that should be design decisions.You've never worked on a large university campus have you?
I din't say it was a good idea, I said I thought I had heard it had changed, I'm trying not to invest in a 2020 code book
Roger
Only for in the same enclosure. You are still allowed six, but they can’t be in the same enclosure for 2020.Has the requirement changed for later code cycles?
For service disconnecting means. Separate building supplied by a feeder can still have six in same enclosure.Only for in the same enclosure. You are still allowed six, but they can’t be in the same enclosure for 2020.
That is correct for a service but not an outside feeder to another building.Only for in the same enclosure. You are still allowed six, but they can’t be in the same enclosure for 2020.
Interesting. I can see it because it’s not on the utility side.For service disconnecting means. Separate building supplied by a feeder can still have six in same enclosure.
You can't easily shut off the bus bars on service (many cases). you are required to have a barrier over the main lugs of the main breaker.Interesting.