Which picture is that?
Service conductors encased in concrete post #21.
Which picture is that?
Which picture is that?
Am I the only one who gets a little disoriented every time I glance at Rob’s picture?
The black stripes seem to twist. Kinda cool really.
Focus Grasshopper!
Panel is double protected. Fuses and breaker-twice. Overkill, not a problem, but waste of money.
Fuses protect feeder (from disco) and panel. A MLO panel would work. Think about it.....
No, it would make no sense.
Main breaker in panel not even required. You have a main service OCPD in the fused disco. It is protecting the panel already.
Think about it.
Where's the rule that states if the service disconnect is not attached to the structure you have to have a disconnect at the building also?
I cant find it.
JAP>
230.70(A) Location. The service disconnecting means shall be installed
in accordance with 230.70(A)(1), (A)(2), and (A)(3).
(1) Readily Accessible Location. The service disconnecting
means shall be installed at a readily accessible location either
outside of a building or structure or inside nearest the point of
entrance of the service conductors.
Where's the rule that states if the service disconnect is not attached to the structure you have to have a disconnect at the building also?
I cant find it.
JAP>
Where's the rule that states if the service disconnect is not attached to the structure you have to have a disconnect at the building also?
I cant find it.
JAP>
225.32 Location. The disconnecting means shall be installed
either inside or outside of the building or structure served or
where the conductors pass through the building or structure.
The disconnecting means shall be at a readily accessible location
nearest the point of entrance of the conductors. For the
purposes of this section, the requirements in 230.6 shall be
utilized.
Sorry I think this is more accurate
Short answer "yes".So if the meter and fused disconnect were on a rack out in the lot nowhere near the structure another disconnect would not be required at the structure itself?
JAP>
Short answer "yes".
In "real life" Ive the the answer vary by AHJ and by distance how close the two are.
"Nowhere near" will likely mean disconnect at both
What is the rule that would require a disconnect at both locations?
JAP>
225.33
Edit: actually 230 would apply to one, 225 for the second.