Re: dishwasher feed
Originally posted by electricmanscott: You can't use the SA circuits to feed more than one kitchen.
I think you can. I look at SA circuits backwards, in the following sense. I don't start with, "This is an SA circuit, so therefore what can I supply with it?" Rather, I ask, "Is this room a Kitchen? It is a Pantry? Is it a Breakfast Room? Is it a Dining Room?" If I get a "Yes" answer, then I say that all circuits that supply wall, floor, or countertop receptacles in that room are, by definition, "SA circuits."
In this case, when I look at the "Outdoor Kitchenette," I get a "Yes" to the first question. So the circuits that supply the receptacles in that space are, by definition, SA circuits. Nothing prevents me from supplying those receptacles with one of the five SA circuits that presently serve the indoor kitchen (i.e., the two required circuits and the three extras supplying one duplex receptacle each).
Nothing in the NEC prohibits a single family dwelling unit from having more than one kitchen.
(You can't use the SA circuits) . . . to feed outdoor receptacles.
Here again, I must disagree. Nothing in the NEC says that a kitchen must be indoors.
NOTE: The receptacles in the outdoor kitchen have to all be GFCI, even if their counterparts in the indoor kitchen do not have to be GFCI.