LarryFine
Master Electrician Electric Contractor Richmond VA
- Location
- Henrico County, VA
- Occupation
- Electrical Contractor
Re: dishwasher feed
"(B)(3) Kitchen Receptacle Requirements.
No small-appliance branch circuit shall serve more than one kitchen."
However, it also says: "...either or both of which shall also be permitted to supply receptacle outlets in the same kitchen and in other rooms specified in 210.52(B)(1)."
So the solution is to consider the outside room a dining room, and these S.A. circuits will supply receptacles for hot plates, etc., just as they are meant to, which is why dining room receptacles are permitted/required to be on 20a. S.A. circuits to begin with.
Sorry, Charlie. Art. 210.52 says, in part:Originally posted by charlie b:
I think you can.Originally posted by electricmanscott: You can't use the SA circuits to feed more than one kitchen.
"(B)(3) Kitchen Receptacle Requirements.
No small-appliance branch circuit shall serve more than one kitchen."
However, it also says: "...either or both of which shall also be permitted to supply receptacle outlets in the same kitchen and in other rooms specified in 210.52(B)(1)."
So the solution is to consider the outside room a dining room, and these S.A. circuits will supply receptacles for hot plates, etc., just as they are meant to, which is why dining room receptacles are permitted/required to be on 20a. S.A. circuits to begin with.