We do the electrical design for apartment houses. The question came up regarding why can't we put both the dishwasher and disposal on a single 20A circuit plugging both into a single 20A GFCI.
The disposal is rated at 3/4 HP, 6A, 120V.
The dishwasher is 120V, 1.2A motor, and 8.1A total
Both appliances are GE.
Looking at those actual nameplate numbers I see no reason not to put both of them on a single 20A circuit. The dishwasher would plug directly into a GFCI, and the disposal into a switched receptacle sub-fed from the GFCI with both mounted in a 2 gang, non-Metalic outlet box under the sink.
Years ago when I remodeled my own kitchen including a new panel board, I put both appliances on a single 20A circuit and never had an issue. (Didn't need to put them on GFCI back then.)
Saving just one AFCI circuit, wiring, and a GFCI for both appliances in each apartment unit in a 48 unit apartment complex adds up to over $4,800. We are working on 4 or 5 complexes at the moment and that's serious $$$!
Have I missed something? BTW, we are under the 2014 NEC in SC.
Thanks,
RC
The disposal is rated at 3/4 HP, 6A, 120V.
The dishwasher is 120V, 1.2A motor, and 8.1A total
Both appliances are GE.
Looking at those actual nameplate numbers I see no reason not to put both of them on a single 20A circuit. The dishwasher would plug directly into a GFCI, and the disposal into a switched receptacle sub-fed from the GFCI with both mounted in a 2 gang, non-Metalic outlet box under the sink.
Years ago when I remodeled my own kitchen including a new panel board, I put both appliances on a single 20A circuit and never had an issue. (Didn't need to put them on GFCI back then.)
Saving just one AFCI circuit, wiring, and a GFCI for both appliances in each apartment unit in a 48 unit apartment complex adds up to over $4,800. We are working on 4 or 5 complexes at the moment and that's serious $$$!
Have I missed something? BTW, we are under the 2014 NEC in SC.