vectormechanic
Member
We are having an issue with current unbalance on one our generators that I am thoroughly baffled by at this point.
The generator where we are having the problem is a 600V unit rated at 1200kW. It is connected to a liquid filled 1500kVA, 24.9kV/600V ungrounded wye-wye transformer, and goes to the local utility?s substation from there (only about 1/3 of a mile). The problem is a current unbalance that is proportional to generator load. At 1200kW load, a current unbalance of 42% is exhibited from C to A phase. (we are currently running the unit at 700kW, which results in a 10-15% unbalance). After going through the generator itself, we found that it had a PI of only 0.82, so the generator was changed with a used/reconditioned spare. (The original generator that was changed out had also been overhauled/reconditioned) When the unit was put back in service, the exact same unbalance appeared. I put a power recorder on the unit and found the A phase current waveform to have clipping with a notch in the center of the clipping. We thought it was possible (though unlikely) that each generator had the same problem, so the leads were rolled at the generator breaker (A phase generator cables to B phase lug on the breaker, B to C, C to A, etc.) with the thought that if the generator was the problem, the clipped waveform would follow the generator leads.
After restarting the unit, I found that the clipping stayed on A phase. My next thought is that there is a problem with the transformer. We had the transformer tested several months ago while the plant was shut down and being overhauled. However, the tests that were performed were somewhat limited since H0/X0 are internally connected inside the transformer tank and could not be separated to check individual phase windings; it did pass the tests that were conducted. I?ve attached screen shots of the waveforms and phasors of the 600V side of the system.
I have gone through the generator excitation system and have not found any anomalies.
At about 700kW load, the 24.9kV side is exhibiting about a 1kV voltage imbalance. I am unable to look at current on the high side due to limitations of my test equipment.
Any ideas?
The generator where we are having the problem is a 600V unit rated at 1200kW. It is connected to a liquid filled 1500kVA, 24.9kV/600V ungrounded wye-wye transformer, and goes to the local utility?s substation from there (only about 1/3 of a mile). The problem is a current unbalance that is proportional to generator load. At 1200kW load, a current unbalance of 42% is exhibited from C to A phase. (we are currently running the unit at 700kW, which results in a 10-15% unbalance). After going through the generator itself, we found that it had a PI of only 0.82, so the generator was changed with a used/reconditioned spare. (The original generator that was changed out had also been overhauled/reconditioned) When the unit was put back in service, the exact same unbalance appeared. I put a power recorder on the unit and found the A phase current waveform to have clipping with a notch in the center of the clipping. We thought it was possible (though unlikely) that each generator had the same problem, so the leads were rolled at the generator breaker (A phase generator cables to B phase lug on the breaker, B to C, C to A, etc.) with the thought that if the generator was the problem, the clipped waveform would follow the generator leads.
After restarting the unit, I found that the clipping stayed on A phase. My next thought is that there is a problem with the transformer. We had the transformer tested several months ago while the plant was shut down and being overhauled. However, the tests that were performed were somewhat limited since H0/X0 are internally connected inside the transformer tank and could not be separated to check individual phase windings; it did pass the tests that were conducted. I?ve attached screen shots of the waveforms and phasors of the 600V side of the system.
I have gone through the generator excitation system and have not found any anomalies.
At about 700kW load, the 24.9kV side is exhibiting about a 1kV voltage imbalance. I am unable to look at current on the high side due to limitations of my test equipment.


Any ideas?