I've seen it, not as extreme on any POCO service conductors that I can recall, but in particular on a poorly selected/designed feeder on a golf course to a remote maintenance shop. Probably about a 1900 foot run of 2 AWG (been a while but close to that size anyway) aluminum set of conductors feeding the shop. They complained the place had voltage issues for years - but it wasn't just voltage drop you get on simple two wire circuit, but because of the voltage drop on the neutral it would give classic signs of open neutral with dimming of lights on one line and brightening of lights on the other line.
I could see a breaker in that case taking its time to clear a fault, but the neutral shift and voltage drop gave it away.