Do as we say not as we do.

Status
Not open for further replies.

iwire

Moderator
Staff member
Location
Massachusetts
So I find this flexable PVC elbow. It's made up out of two PVC FAs, two carflex connectors and a chunk of carflex.

If I made this myself for sure people would call it a 110.3 violation.
 

Attachments

  • IMG_20161004_001257.jpg
    IMG_20161004_001257.jpg
    148.1 KB · Views: 2
  • IMG_20161004_001201.jpg
    IMG_20161004_001201.jpg
    141.7 KB · Views: 3

Carultch

Senior Member
Location
Massachusetts
So I find this flexable PVC elbow. It's made up out of two PVC FAs, two carflex connectors and a chunk of carflex.

If I made this myself for sure people would call it a 110.3 violation.


I'm not understanding the exact problem. How is it a 110.3 violation?

Is this an issue of NPSM male threads being connected to NPT female threads?
Is this an issue of LFNC being sold as part of a family of PVC fittings? Possibly leading to use in environments where LFNC would not be allowed?

Home Depot's website says it is "ETL and UL listed for safety".
 

JFletcher

Senior Member
Location
Williamsburg, VA
So I find this flexable PVC elbow. It's made up out of two PVC FAs, two carflex connectors and a chunk of carflex.

If I made this myself for sure people would call it a 110.3 violation.

If you made it yourself, would you spend more money?

No 110.3 violation from me. You may pass go, and collect $200.
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Violation or not, I can't think of a place I would use them. After a year or two in the sun carflex isn't all that flexible, the gaskets will be rotted away and if I bury, sch 40 is easy enough to bend.

I haven't seen them pushed at any of my supply houses. For DIYers only.
 

kwired

Electron manager
Location
NE Nebraska
110.3B simply means usage according to listing.....

~RJ~
Exactly, one can use all the same components to build a similar thing and still be within the listing of those components. This just happens to be an assembly that is listed as is.

How is it any different then using a rigid (PVC or metallic) raceway and short section of flex for various reasons? Maybe where there is slight movement between components and flexibility is required. Most of us wouldn't use this where no flexibility is needed, but it would be code legal whether field made or by purchasing this assembly.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The difference is the flex elbow is listed. I bet most inspectors would accept a setup that you put together with 2 carflex connectors and threaded couplings
 

iwire

Moderator
Staff member
Location
Massachusetts
The difference is the flex elbow is listed.

Exactly

I bet most inspectors would accept a setup that you put together with 2 carflex connectors and threaded couplings

Most? In my area for sure. But that still leaves a great many that would have a problem with it.

I make up my own changeovers all the time but on these forums we see the same questions come up time and again about using fittings in ways not directly intended for.
 

kwired

Electron manager
Location
NE Nebraska
Exactly



Most? In my area for sure. But that still leaves a great many that would have a problem with it.

I make up my own changeovers all the time but on these forums we see the same questions come up time and again about using fittings in ways not directly intended for.
What is not being for what it is intended for - even if you build your own "flex coupling"?

The flex connector made to connect to the flex, and the female PVC adapter is made to accept a male thread on one end and be cemented to PVC conduit on the other end the last I knew. I don't think we run into the straight vs tapered thread issues with these fittings like you can run into with metal raceway fittings, and certainly not how it relates to grounding and bonding abilities.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
It lists UL file number E 171248.
PS It is listed under QQYZ "Wiring Assemblies." The first sentence of the guideinfo is "This category covers prefabricated wiring systems comprised of certified electrical components that could be field assembled and inspected by an Authority Having Jurisdiction (AHJ), but are assembled in the factory prior to field installation."

Cheers, Wayne
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
PS It is listed under QQYZ "Wiring Assemblies." The first sentence of the guideinfo is "This category covers prefabricated wiring systems comprised of certified electrical components that could be field assembled and inspected by an Authority Having Jurisdiction (AHJ), but are assembled in the factory prior to field installation."

Cheers, Wayne

Right there is the money quote. A field assembly would be just as acceptable and NOT a violation.
 

iwire

Moderator
Staff member
Location
Massachusetts
It seems I may be misunderstood.

My position is it should not a be violation of any kind.

The reality is that on these forums we hear of electricians being shot down for this very type of thing.
 

kwired

Electron manager
Location
NE Nebraska
It seems I may be misunderstood.

My position is it should not a be violation of any kind.

The reality is that on these forums we hear of electricians being shot down for this very type of thing.
We hear of a lot of things being shot down that just don't make sense to many. Inspectors come in smart versions as well as not so smart versions just like electricians do:D
 

Carultch

Senior Member
Location
Massachusetts
So I find this flexable PVC elbow. It's made up out of two PVC FAs, two carflex connectors and a chunk of carflex.

If I made this myself for sure people would call it a 110.3 violation.

Can you explain what the actual problem is? And is it an issue with just not complying with the letter of the code, or a real life physical consequence?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
It seems I may be misunderstood.

My position is it should not a be violation of any kind.

The reality is that on these forums we hear of electricians being shot down for this very type of thing.
That is because no male connector has ever been evaluated for use with female threads. Some AHJs see that as a use outside the listing and a 110.3(B) violation.

It is something I have done thousands of times. I would bet a very small percentage of the LFMC connectors that I have installed have been used in the way that they have been evaluated for...that is with lock nuts.
 