dossrc1
Member
- Location
- Kennedy Space Center, Florida
Comments to 210.8 (C)
Comments to 210.8 (C)
Morning everybody...just saw this thread and thought it was pretty interesting. If anyone has a NEC 2014 Handbook, there is a very good explanation after the Code Section...
It specifically answers you Question Dave...
"The GFCI requirement only applies to dwelling unit locations and to boat hoist supplied by 15 - 20a branch circuits rated @ 240v or less. It is very important to note that it applies to ALL OUTLETS, not just to receptacle outlets. Therefore, both Cord-and-Plug Connected and Hard-Wired Boat Hoist are required to be GFCI protected."
If you can get ahold of a "NEC 2014 Handbook" they really explain articles such as this...
Hope this helps...
Rob
Comments to 210.8 (C)
Morning everybody...just saw this thread and thought it was pretty interesting. If anyone has a NEC 2014 Handbook, there is a very good explanation after the Code Section...
It specifically answers you Question Dave...
"The GFCI requirement only applies to dwelling unit locations and to boat hoist supplied by 15 - 20a branch circuits rated @ 240v or less. It is very important to note that it applies to ALL OUTLETS, not just to receptacle outlets. Therefore, both Cord-and-Plug Connected and Hard-Wired Boat Hoist are required to be GFCI protected."