: then I don't see why you would bond the transformer ground and neutral. The neutral (at the transformer) would be solidly connected to the service neutral, and the ground (at the transformer) would be solidly connected to the service ground.
Seems to me the N-G bond at the service would be the only one required.
Steve
What is the secondary voltage of the transformer. i assume it is 208/120 3 phase 4-wire to match the service voltage.
That is correct.
Steve, the transformer is required to have the bonding jumper installed at the source of the SDS or at the first OCPD.
Steve, that is thinking out of the box, but i don't think you can get around the definition of SDS. "A premises wiring system whose power is derived from a source of electric energy or equipment other than a service".(period)IMO since the transformer meets the definition, 250.30 applies.If it has a solid neutral connection to the utility service, then I don't believe it is an SDS, so the bonding jumper isn't required at the transformer or the first OCPD.
Steve
Steve, that is thinking out of the box, but i don't think you can get around the definition of SDS. "A premises wiring system whose power is derived from a source of electric energy or equipment other than a service".(period)IMO since the transformer meets the definition, 250.30 applies.
Rick
Steve, that is thinking out of the box, but i don't think you can get around the definition of SDS. "A premises wiring system whose power is derived from a source of electric energy or equipment other than a service".(period)IMO since the transformer meets the definition, 250.30 applies.
Rick
But read the next sentence also:
"Such systems have no direct electrical connection, including a solidly connected grounded circuit conductors, to supply conductors originating in another system."
Steve
Perhaps tomorrow (or should I say later today?), after we get some more info...
"Tomorrow" is here....
I drew up a one-line but it doesn't seem to indicate enough info...
So I drew up a connection diagram...
View attachment 3045
Ok, that is it in a nut shell. So please explain how we can take a delta transformer, create a wye system and not have a seperately derived system. I see your point but like Rick said I believe I'll have a hard time selling it to the inspector.