Where does the code specify primary heat source. I have put the heater part on a t-stat in the past.
Okay I will concede that it could be considered space heating, then you would have to reconcile the following statement with 424.3(B).
In general the heat is required to be 125% but not the light & fan. All that doesn't matter if the manufacturer requires a 20 amp cir anyway and I believe the calc. would still be over 15 amps
424.3 Branch Circuits.
(B) Branch-Circuit Sizing. Fixed electric space-heating
equipment and motors shall be considered continuous load.
And if the fan and heat are considered continuous, then the light is considered.......?