Pierre C Belarge said:
All of the circuit components are required to be rated for 90 degree C, that would also mean the enclosure.
Not necessarily.



Use of compression connectors (e.g. Ilsco's) on the ends of the conductors satisfy the direct requirements of 110.14(C)(2). Once the barrel terminal is installed the requirements of 110.14(C)(1)(a) & (b) are [somewhat] moot and the terminal to equipment connection is beyond the scope of conductor termination. The FPN after 110.14(C)(2) referencing 110.14(C)(1 & 2), so it depends on the markings and listing of the equipment.
 