Jim W in Tampa
Senior Member
- Location
- Tampa Florida
Are there any exceptions that would not require a disconnect.This is one that control box is inside and 1 hp 3 phase 208 motor is outside and would not be in site.
Jim W in Tampa said:Are there any exceptions that would not require a disconnect.This is one that control box is inside and 1 hp 3 phase 208 motor is outside and would not be in site.
I would use (A).Hazard area with trucks backing into area.iwire said:Rick which condition would you use a or b?
.
RUWired said:I would use (A).Hazard area with trucks backing into area.
After reading all the fine print notes and examples,i would agree.How about we post a note on the door to keep open while servicing the motor:grin:iwire said:That is not what 430.102(B) Exception: (a) allows...IMO.
RUWired said:After reading all the fine print notes and examples,i would agree.How about we post a note on the door to keep open while servicing the motor:grin:
No, the disconnect must open the power conductors to the equipment. See 430.103.Would a single pole switch that is in series with the 110 volt coil on the contactor be qualified as a disconnect ?