Does a metal tin ceiling have to be bonded?

Status
Not open for further replies.

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
I’m working on a cook shed for a friend; the ceiling is tin with recessed lighting.

He told me today the inspector had mentioned something about bonding the tin.

Is there an NEC requirement for this?

1c623987d54b10dd3d5647f1b4104e41.jpg



Sent from my iPhone using Tapatalk
 

low-wattage

Member
Location
Pennsyltucky
You have 250.4(A)(4)

(4) Bonding of Electrically Conductive Materials and Other Equipment. Normally non–current-carrying electrically conductive materials that are likely to become energized shall be connected together and to the electrical supply source in a manner that establishes an effective ground-fault current path

The sheets have to be

* connected together - they're connected at the seam, so that's covered

* connected to the electrical supply source - I could see this going either way ... if the sheets are on the top of the rafters, they could be floating and need a jumper somewhere to something bonded. If you had roof sheets screwed into the top of bar joist type trusses, and electrical conduits and boxes bolted to the trusses, I would think that's a good bond.

* in a manner that establishes an effective ground fault current path - this seems subjective, are the seams a good enough bond? If you have overlapping sheets of bare galvanized corrugated tin, that seems like a very good electrical connection, if the sheets are epoxy coated and the screws are coated with some climate seal, maybe not.
 

jap

Senior Member
Occupation
Electrician
You have 250.4(A)(4)



The sheets have to be

* connected together - they're connected at the seam, so that's covered

* connected to the electrical supply source - I could see this going either way ... if the sheets are on the top of the rafters, they could be floating and need a jumper somewhere to something bonded. If you had roof sheets screwed into the top of bar joist type trusses, and electrical conduits and boxes bolted to the trusses, I would think that's a good bond.

* in a manner that establishes an effective ground fault current path - this seems subjective, are the seams a good enough bond? If you have overlapping sheets of bare galvanized corrugated tin, that seems like a very good electrical connection, if the sheets are epoxy coated and the screws are coated with some climate seal, maybe not.


:unsure:

JAP
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
So every metal roof on a building with electricity has to be bonded??
I haven’t ever bonded a metal roof on a house. Doubt many others have either.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
So every metal roof on a building with electricity has to be bonded??
I haven’t ever bonded a metal roof on a house. Doubt many others have either.
It seems like something that someone forgot about. Maybe someone should suggest a change to the code to require metal roofing and siding to be bonded to the GES with a #6 conductor. :)
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
You have 250.4(A)(4)



The sheets have to be

* connected together - they're connected at the seam, so that's covered

* connected to the electrical supply source - I could see this going either way ... if the sheets are on the top of the rafters, they could be floating and need a jumper somewhere to something bonded. If you had roof sheets screwed into the top of bar joist type trusses, and electrical conduits and boxes bolted to the trusses, I would think that's a good bond.

* in a manner that establishes an effective ground fault current path - this seems subjective, are the seams a good enough bond? If you have overlapping sheets of bare galvanized corrugated tin, that seems like a very good electrical connection, if the sheets are epoxy coated and the screws are coated with some climate seal, maybe not.
Well, here they clearly aren't, unless they are cleverly disguising metal bars joists as wooden roof joists.
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
You have 250.4(A)(4)



The sheets have to be

* connected together - they're connected at the seam, so that's covered

* connected to the electrical supply source - I could see this going either way ... if the sheets are on the top of the rafters, they could be floating and need a jumper somewhere to something bonded. If you had roof sheets screwed into the top of bar joist type trusses, and electrical conduits and boxes bolted to the trusses, I would think that's a good bond.

* in a manner that establishes an effective ground fault current path - this seems subjective, are the seams a good enough bond? If you have overlapping sheets of bare galvanized corrugated tin, that seems like a very good electrical connection, if the sheets are epoxy coated and the screws are coated with some climate seal, maybe not.

I appreciate you finding this code to discuss.

Reading this, it seems to me the EGC to the fixture would provide the path to ground in case of a fault. My interpretation would be that this ceiling isn’t likely to become energized by something other than the fixtures, which again, are grounded.

Any thoughts on that?


Sent from my iPad using Tapatalk
 

Charged

Senior Member
Location
Ohio
Occupation
Electrical Designer
Check the local building code . In Ohio the OBC has a requirement in the electrical section to bond metal veneer on structures.
 