Does a metal tin ceiling have to be bonded?

Status
Not open for further replies.

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
120v to center point of xfmr?

Presumably in addition to actual soil.

Remember we have an intentionally grounded electrical system, and the midpoint of the transformer is connected to earth and all bonded metal.

This means that the transformer ungrounded conductors are at 120V relative to midpoint _and_ soil.

If you have an ungrounded conductor faulted to unbonded metal, that metal will be at 120V relative to soil.

Jon
 

wyreman

Senior Member
Location
SF CA USA
Occupation
electrical contractor
No, literal earth. Dirt. Ground. One probe into dirt and other onto metal siding. Soil was very moist. Isolated issue to one circuit and turning that off voltage disappeared.
wiggie! =0

I had a good sniffer one time that used a big copper plate in the dirt
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
wiggie! =0

I had a good sniffer one time that used a big copper plate in the dirt
Not sure what you mean. My helper had gotten zapped off the door handle on the metal trailer door. That is why I tested. A wiggie wouldn't have changed that. Even showed as hot with the hot stick.
 

wyreman

Senior Member
Location
SF CA USA
Occupation
electrical contractor
I had a wire tracing / pipe tracing tool at work one time, looked like a metal detector
One alligator went to a big copper plate you had to wedge down in the earth, the other alligator went to the wire or pipe.
and then you could ring the pipe pretty good.
I'm agreeing with you.

I had lots of those where someone gets zapped by touching two things.
What two things was your helper touching? door handle and... barefoot?
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
A different inspector came for my final, and didn’t mention anything about bonding the tin ceiling.

And it turned out pretty nice !


173b780a6aad04cef2b6f091b32970b4.jpg



Sent from my iPhone using Tapatalk
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
A different inspector came for my final, and didn’t mention anything about bonding the tin ceiling.

And it turned out pretty nice !


173b780a6aad04cef2b6f091b32970b4.jpg



Sent from my iPhone using Tapatalk
Looks very nice! Is the tin we see also the functional roof? I ask because I see a lot of rust on the panels. Which is fine for ambience if it's not part of the weather envelope.
 

Bjenks

Senior Member
Location
East Coast of FL
I put this in my general wire methods and material notes. I do this because I have had many plan reviewers ask me to make sure the contractor is aware so now I just put it as part of my notes. It is part of the Florida Building Code and is really more about metal framing that can be energize when a drywaller put a screw in the electric and touches the metal framing but if you are running romex up there I can see where they would require it, but just put a metal j-box up there and have it touch the roof:
"METAL FRAMING MEMBERS SHALL BE BONDED TO THE EQUIPMENT GROUNDING CONDUCTOR FOR ANY CIRCUIT THAT MAY ENERGIZE THE BUILDING FRAMING AND BE SIZED IN ACCORDANCE WITH THE NATIONAL ELECTRIC CODE, TABLE 250.122. FOR THE PURPOSE OF THIS REQUIREMENT, A GROUNDED METAL OUTLET BOX ATTACHED TO THE FRAMING SHALL BE PERMITTED"
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
Looks very nice! Is the tin we see also the functional roof? I ask because I see a lot of rust on the panels. Which is fine for ambience if it's not part of the weather envelope.

No, this tin is on the bottom of wood trusses, standing seam metal roof on top.

8cf316d93319cfae21d137a3c48220b1.jpg



Sent from my iPhone using Tapatalk
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
I put this in my general wire methods and material notes. I do this because I have had many plan reviewers ask me to make sure the contractor is aware so now I just put it as part of my notes. It is part of the Florida Building Code and is really more about metal framing that can be energize when a drywaller put a screw in the electric and touches the metal framing but if you are running romex up there I can see where they would require it, but just put a metal j-box up there and have it touch the roof:
"METAL FRAMING MEMBERS SHALL BE BONDED TO THE EQUIPMENT GROUNDING CONDUCTOR FOR ANY CIRCUIT THAT MAY ENERGIZE THE BUILDING FRAMING AND BE SIZED IN ACCORDANCE WITH THE NATIONAL ELECTRIC CODE, TABLE 250.122. FOR THE PURPOSE OF THIS REQUIREMENT, A GROUNDED METAL OUTLET BOX ATTACHED TO THE FRAMING SHALL BE PERMITTED"

Its wood framing. The tin is just sheathing on wood trusses.
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
That's frickin beautiful. (y)

JAP>

I agree. Everyone did a really nice job. There was a little more to the overall project than just that building. There’s a bunk house we added, and the larger main residence was built 5/yrs ago. I did some additional work adding wired networking between all the structures, Luxul router and AP’s at each structure, and Sonos audio.

d5f5815325eb2baf086f8851b27f3b5f.jpg


2c247415924f4a87d3be94ff15301d76.jpg



82e21c99b5531d2a08f9356480fb042a.jpg



Here’s a video I took yesterday playing with the audio.



Sent from my iPhone using Tapatalk
 