radiopet
Senior Member
- Location
- Spotsylvania, VA
(the grounded conductor is installed in one of the multiple raceways)
The service is a 480Y/277Volt, 3 phase - 2000A service.
Most of the building loads are 3phase, not requiring a grounded conductor.
The engineer who designed this had 1 grounded conductor on the prints, to supply the GFPE unit that protects the service as per 230.95.
I had issues with this setup, and we had a meeting of all the 'minds' on the site.
250.24(C) Requires a grounded conductor brought to the service.
250.24(C)(1) requires the sizing to be 12.5% of the ungrounded conductors of this size service.
The result was to reinstall the conductors, with a grounded conductor installed in each raceway.
The engineer is a very young gentleman, who is fairly new in the field. He had a handbook that was well highlighted and lots of notes. We spoke in private after the meeting. He mentioned to me that this was the first of (8) sites that an inspector actually caught this installation issue. After he finally understood how important it is, he was concerned about the other locations. I suggested he go back to the office and bring it up in a meeting.
He called me a few weeks later to tell me they were going back to the sites to change out the other services. I bet he will not make this mistake again.
(There is lots of other cool stuff I got to experience on this site, other than the service)
I was getting ready to post just those references....We would have caught that on plan review...we catch worse than this on plan review which got me cussed out by an engineer yesterday.....asked that I never review his plans again sad to say. So I sat down and did his other one waiting review...