250.148 would contain requirements for bonding the box to the EGC. If there is no EGC pulled in the raceway then the raceway would have to be the EGC, and should inherently bond to the box via the raceway termination to the box.
If you are asking about a jumper from the box to the receptacle - that is covered in 250.146. A summary of that is that if there is metal to metal contact between the receptacle yoke and the box (presumed to be connected to be bonded to the EGC) then that connection is suitable for bonding the receptacle, or specially designed devices(often called self grounding) can be allowed to do the bonding in cases where there is not direct metal to metal contact between device and box. Raised device covers that meet requirements in 250.146(A) can also be used without any additional bonding jumpers for providing EGC to the device and it doesn't matter if a EGC has been pulled in raceways or not, but if they have been pulled they must have a connection to the box if the box contains splices, devices or other connections involving the contained conductors.
I did see that in the Mike Holt book, and it said it was for the purpose of working on the receptacle without breaking the ground fault circuit.