I'm doing work for a client designing a facility with UPS backup.
This is what the client wants to do:
They are basically suggesting having one panelboard fed directly from the utility, and one fed from the UPS, then run wire from both and connect them to the same outlet, for "redundancy" as they put it. Does this seem like a bad idea to anyone else but me?
As I understand it, they'd have to make damn sure they connected the same phases (since they're 3-phase panelboards). But even then, if the power from the UPS inverter leads or lags the power coming from the other panelboard, even a little bit, wouldn't that be disasterous?
Thank you. I'm trying find a nicer way of telling the client this :smile:I don't consider this a bad idea. It is outright stupid.
Thank you. I'm trying find a nicer way of telling the client this :smile:
Yeah, +1 on the stupid.
However, as noted above, all is not lost; you could add a second receptacle everyplace there is one receptacle, with the second feed serving the second receptical, and ensure that every device in the data centre has dual power inlets and plug one inlet to each receptacle.
and I see no benefit over just having the one receptacle backed up by the UPS.
Unless the UPS is a very expensive unit it does not output a true sine wave, so its output could never be synced with the utility.
Only UPS's that have static bypasses are synced with the utility. Most small UPS's do not contain bypass circuitry.UPS outputs are always sync'd to the utility because UPSs have really poor fault clearing capability, so they need to be able to static switch back to utility power to clear downstream faults. If the UPS and utility aren't in sync then static switching isn't going to be pretty.
Only UPS's that have static bypasses are synced with the utility. Most small UPS's do not contain bypass circuitry.
Don't all UPS systems have battery backup? I thought that was what makes them "uninterruptible power supplies".UPS systems that have battery backup are standby systems
I would also cite 210.7(B)Multiple circuits.
Why would they be "synced"? They don't parallel their output with the utility. They close a switch to provide battery power to the loads from the inverter after the sense the loss of utility power. The do not have a "closed" transition back to the utility power after it has been restored.Most small UPSs are not double conversion and thus must be mains synced.
Seriously - I've never seen or heard of a UPS that doesn't sync to the incoming mains from toys that kick round on the floor at home, to 2MW serious modular UPS systems. ...
I guess I am thinking the OP would be a personal/small office/network server style. There are many smaller units that are used in stand-alone applications and are not maintanable while energized.Thats not to say they dont exist - maybe they do, but I've never seen one. But you couldn't use a UPS that doesn't sync in any sort of situation where you want any form of bypass static, relay or manual. That must be a very small market segment.