Second my question about the UPS being synced to the utility was addressed a statement made by another member that said "all UPS's are synced to the utility. I don't believe that is a correct statement and I am not sure it is even possible given the output type of some of the small plug and play systems that are often used.
That would be me
Its only double conversion UPSs where one gets the theoretical choice of whether to sync or not sync, as the inverter mechanism is separate and distinct from the incoming supply during normal operation. All other types of UPS dont have the capability to not have the output syncronised tothe input when the input is present. Most serious size UPSs (from a few KVA up) are double conversion.
Smaller UPSs either use a single transformer for both battery charging and inverting, and so that transformer is by definition absolutely in phase with the mains supplying it, and thus the output of the UPS is syncronised tothe mains feed. Another sort uses the big transformer and inverter only when incoming power has failed and normally the incoming power is static switched to the outgoing sockets. There is a smaller transformer for battery charging. Should the supply fail then the inverter starts up in phase with then lost incoming power and takes the outgoing load.
If there are any examples where there are unsyncronised UPSs I'd really like to know about them. My curiosity is piqued!
The only time this type of technology is used with the output unsyncronised to the incoming power is where you have 60Hz in and want 50Hz out and then you dont want a bypass at all! Often this type of "UPS" isn't a UPS at all, it has no batteries, its just used for frequency conversion.
In its normal form, rotary (flywheel) UPSs stay syncronised too. But they are a whole different (and facinating) kettle of fish...