Doorbell conductor, 18\2

Status
Not open for further replies.

865resi

Member
Location
Tennessee
Occupation
Electrician
Are we allowed to put the 18\2 in the same drilled hold with 14\2? There is such a small space between the door and window and so many 14\2 and 14\3 that it is ridiculous. 2017 code. Have a great day. Thank you.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
725.136(I)(1) Either all of the electric light, power, Class 1, non–power-limited fire alarm and medium-power network-powered broadband communications circuit conductors or all of the Class 2 and Class 3 circuit conductors are in a raceway or in metal-sheathed, metal-clad, non–metallic-sheathed, Type TC, or Type UF cables
 