Double Neutral

Status
Not open for further replies.

bphgravity

Senior Member
Location
Florida
Can you be more specific? Do you mean installing a grounded (neutral) conductor twice its required size, or do you mean installing two neutral conductors?
 
B

Barry G

Guest
2 neutral conductors.
The panel schedule states: Provide w/equipment and insulated isolated ground bus and a double neutral (sorry, I should have added that).
 
Last edited:

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Sounds as though they are asking for a 200% neutral, this means the neutral bar will be set up with double barrel lugs or atleast a lug that will accept two conductors for the paralleled neutral.

The reason for this is the designers anticipation of additive harmonics on the neutral due to nonlinear loads.

Roger
 
Status
Not open for further replies.
Top