Double pole vs single pole

Status
Not open for further replies.
If you have line and load conductors reversed newer units will not reset either, fairly certain this is a listing requirement.

That very well could have been the issue, it was a pre existing problem at a friends house. I may have over looked that initially and then when I replaced it wired it correctly and it was able to reset, and then when I placed the old one on it worked as well cuz I did that one correctly too


Sent from my iPhone using Tapatalk

Hmmm, post #12 must have been invisible.;)
 
then what exactly is their "single pole" as listed in their PDF products guide ??
I don't know for sure but like a single pole switch will only turn off the hot but a double pole will turn off the hot and neutral, maybe the single pole GFCI only disconnects the hot, but the two pole GFCI disconnects both the hot and neutral. BTW, first post.
 
:thumbsup::thumbsup::thumbsup:

FWIW the 5-15 receptacle is sometimes referred to "two pole three wire"

If a receptacle were "single pole" it would just be one conductor that connects to whatever plug matches it.

I agree they typically use the word pole to describe the number of wires connected excluding the EGC. Here's the listing for a L14-30R:

SELECTSPEC Product Type Locking Devices
Locking Device Product Receptacle
Locking Device Rating 30A, 125/250V
Locking Device Wiring Scheme 3 Pole, 4 Wire Grounding
Locking Device NEMA Configuration L14-30R
 
then what exactly is their "single pole" as listed in their PDF products guide ??
P&S wiring devices guide? Single pole GFCI receptacle?


Don't know what product you are referring to, but the way GFCI's work, there must be at least two circuit conductors monitored.
 
I don't know for sure but like a single pole switch will only turn off the hot but a double pole will turn off the hot and neutral, maybe the single pole GFCI only disconnects the hot, but the two pole GFCI disconnects both the hot and neutral. BTW, first post.

A single pole switch interrupts one conductor whether it be a "hot conductor" or a grounded conductor. Code doesn't allow you interrupt the grounded conductor only in most instances though.

Makes sense to me for GFCI to interrupt all conductors of the circuit it protects. If it is intended to trip on a neutral to ground fault, it only makes sense that it interrupt the neutral, or else it never opened the fault current path it responded to.
 
but it was mentioned, dont all gfci recepts have a switch contact on N & L wires ??


US06191589-20010220-D00000.png
 
Makes sense to me for GFCI to interrupt all conductors of the circuit it protects. If it is intended to trip on a neutral to ground fault, it only makes sense that it interrupt the neutral, or else it never opened the fault current path it responded to.
On the contrary, interrupting the hot of a hot to ground fault will clear the fault just fine, and interrupting only the hot will stop any objectionable current on a neutral to ground fault.
I suspect that a more important reason is that if the unit is miswired, with hot and neutral reversed, the two-pole GFCI will still do its job of preventing injury.



Sent from my XT1585 using Tapatalk
 
On the contrary, interrupting the hot of a hot to ground fault will clear the fault just fine, and interrupting only the hot will stop any objectionable current on a neutral to ground fault.
I suspect that a more important reason is that if the unit is miswired, with hot and neutral reversed, the two-pole GFCI will still do its job of preventing injury.



Sent from my XT1585 using Tapatalk
What is the point of detecting neutral to ground faults, even in no load situations then?

Isolation of the neutral when tripping will reduce "stray voltage" shock incidents to some degree. Especially when around swimming pools, marinas and similar situations. Don't know if that is why they open the neutral with typical GFCI's, but often assumed it was at least partly why. Also can't recall ever seeing one that didn't open the neutral.
 
The normal operation of the differential current transformer forces you to detect neutral to ground faults under load whether you want to or not.
The additional specific neutral/ground fault detection in the GFCI receptacle just adds detection of such faults upstream even before a load is applied.
You are correct that some small offset from ground in exposed metal surfaces can result, especially under heavy load. `
 