GeorgeB
ElectroHydraulics engineer (retired)
- Location
- Greenville SC
- Occupation
- Retired
Industrially, we have 2 wire, 3 wire, and 4 wire sensing devices (proximity and photoelectric for example) that use "some" line power. The 2 and 3 wire could both use the "coil" as the power supply. With the 3 wire, the output might either be "sourced" or "sinked", connected to hot or ground. The 4 wire USUALLY are "dry contact".Is there such thing as a relay where the coil is also a power supply? For example, the coil itself provides the 24VDC used to monitor a dry contact, and when that contact closes, the current in the circuit activates the coil on the relay then closes the dry contact that belongs to the relay? In the end, it would just save getting an external power supply...
As others have said, when a device requires a dry contact, it is supplying whatever power it needs. The advantage is that the "relay" can have an AC or DC coil of virtually any voltage. Isolation is assumed.
Whet is not mentioned is that there is a difference in contacts being dry (unpowered) and "dry circuit rated". Often a very low current must be switched; in my electro-hydraulic activities, this is often an analog signal, as into an inverter or servo amplifier. Contacts rated 15 amps usually work for a short period before the resistance becomes an issue. From the old telephone days, "crossbar" contacts, usually of noble metals (palladium or gold commonly) are used ... 1 microamp "wetting" current is not uncommon. Look at, for example, needing to reliably source 10 mV (3 rpm on a 10V=3000 rpm) into a 10k input impedance ... 0.1 microamp ...