?Primary voltage is the low voltage side.
A question? This is a step up transformer.
Where did you come up with that information? I missed it.A question? This is a step up transformer.
ooooo. NM.Where did you come up with that information? I missed it.
Can you post a photo of the transformer nameplate so we can look at the taps?
Yes I can tomorrow when I show up back on-site.
ooooo. NM.
Maybe posts 4 & 5.
In case you wondering how the math works.
With a ratio of 2.3
480/208=2.3
512/2.3= 222.6 primary voltage
If you want to do it the other way
208 to 480
208/480= .433
1/.433= 2.3
A pic of the tag will confirm your transformer set up. It will also give a list of taps which you can change to correct the output voltage if need be.
Look forward to what you find.
That nameplate shows a delta configuration on the high side with no neutral. Aren't the fixtures in question 277 volts?
Where are you getting it?There’s is a neutral
Also if it were corner grounded the voltage would be 480 to ground on two legs.If this transformer is being used to step up 208/120 V to 480 V, there cannot be any 277 V loads on the 480 V delta winding because there is no neutral. If the 480 V "neutral" is connected to ground at the transformer, then this is a big mess.