In case you wondering how the math works.
With a ratio of 2.3
480/208=2.3
512/2.3= 222.6 primary voltage
If you want to do it the other way
208 to 480
208/480= .433
1/.433= 2.3

A pic of the tag will confirm your transformer set up. It will also give a list of taps which you can change to correct the output voltage if need be.
Look forward to what you find.
 
Have you checked the voltage to ground (277) on all three phases....
From that nameplate you should not have a true neutral.
 
The high-voltage side is delta/no neutral, and the low-voltage side is wye/with neutral.

If you're using this as a step-up transformer, your output will not have a neutral.

Thus, any line-to-ground voltages you're getting are meaningless and not usable.
 
If this transformer is being used to step up 208/120 V to 480 V, there cannot be any 277 V loads on the 480 V delta winding because there is no neutral. If the 480 V "neutral" is connected to ground at the transformer, then this is a big mess.
 
If this transformer is being used to step up 208/120 V to 480 V, there cannot be any 277 V loads on the 480 V delta winding because there is no neutral. If the 480 V "neutral" is connected to ground at the transformer, then this is a big mess.
Also if it were corner grounded the voltage would be 480 to ground on two legs.
 
I'm thinking that if there is a 480Y/277 volt panel feeding the lighting the nameplate in post #30 is not the correct one.
 