Dry type transformer

Status
Not open for further replies.

packersbay

Member
Location
New mexico
Occupation
Electrician
In case you wondering how the math works.
With a ratio of 2.3
480/208=2.3
512/2.3= 222.6 primary voltage
If you want to do it the other way
208 to 480
208/480= .433
1/.433= 2.3

A pic of the tag will confirm your transformer set up. It will also give a list of taps which you can change to correct the output voltage if need be.
Look forward to what you find.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Have you checked the voltage to ground (277) on all three phases....
From that nameplate you should not have a true neutral.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
The high-voltage side is delta/no neutral, and the low-voltage side is wye/with neutral.

If you're using this as a step-up transformer, your output will not have a neutral.

Thus, any line-to-ground voltages you're getting are meaningless and not usable.
 

David Castor

Senior Member
Location
Washington, USA
Occupation
Electrical Engineer
If this transformer is being used to step up 208/120 V to 480 V, there cannot be any 277 V loads on the 480 V delta winding because there is no neutral. If the 480 V "neutral" is connected to ground at the transformer, then this is a big mess.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If this transformer is being used to step up 208/120 V to 480 V, there cannot be any 277 V loads on the 480 V delta winding because there is no neutral. If the 480 V "neutral" is connected to ground at the transformer, then this is a big mess.
Also if it were corner grounded the voltage would be 480 to ground on two legs.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I'm thinking that if there is a 480Y/277 volt panel feeding the lighting the nameplate in post #30 is not the correct one.
 