If the nameplate is correct, you cannot use wye-wired loads on the high voltage side. Period!
If it were not for that problem, all you would have to do is change the taps on the high voltage side to lower the voltage.
Since the taps are on the secondary side in this configuration they cannot serve to prevent core saturation from excessive primary voltage.
If it were not for that problem, all you would have to do is change the taps on the high voltage side to lower the voltage.
Since the taps are on the secondary side in this configuration they cannot serve to prevent core saturation from excessive primary voltage.