And chances are hight that if only using 1 burner that it will not trip.
That reasoning works the other way also, holiday time with most or all burners on and it probally would trip.
And chances are hight that if only using 1 burner that it will not trip.
I have a costumer who does not want to pay me to run a circuit for a second range in the basement. She wants me to tap off of the dryer circuit.
I was looking through 210 and from all that I saw, I am probably not allowed to do that unless I put each on a receptacle.
I really don't want to do it. Are there any code issues that you think I should be aware of:-?
Thanks,
220.14(A). Dryer outlet~5000W, Range outlet~8000W.
220.18 The total load shall not exceed the rating of the branch circuit ...
5000+8000=13000. 13000/240=54A circuit needed.
210.21(B)(3). A 30 amp receptacle not allowed on a 50 amp circuit.
Can't do it.
Volta, where do you see in 220.14(A) that a dryer outlet is 5000W and a range outlet is 8000W? I don't see that. I see that loads for dryers and household cooking appliances shall be permitted to be as specified in 220.54 and 220.55 (220.14(B)).
220.54 does say a dryer shall be calculated at not less than 5000W (but to use the nameplate if it is higher than 5000W.) Per 220.55, you can use the nameplate rating of the range, OR use the demand factors in table 220.55.
If the nameplate of the range is 2500W, and you use the 80% demand factor in column A, then the range demand is 2000W.
2000W+5000W=7000W which is 29.17A. That would be allowed on a 30A circuit.
Care to tell us where we can get a range that only needs 2500 ?
Volta, where do you see in 220.14(A) that a dryer outlet is 5000W and a range outlet is 8000W? I don't see that. I see that loads for dryers and household cooking appliances shall be permitted to be as specified in 220.54 and 220.55 (220.14(B)).
220.54 does say a dryer shall be calculated at not less than 5000W (but to use the nameplate if it is higher than 5000W.) Per 220.55, you can use the nameplate rating of the range, OR use the demand factors in table 220.55.
If the nameplate of the range is 2500W, and you use the 80% demand factor in column A, then the range demand is 2000W.
2000W+5000W=7000W which is 29.17A. That would be allowed on a 30A circuit.
It's the owner's house, not yours. If what they are requesting is not in violation of the code, why would you have an issue with it?
For the range, as you said, 220.14(B) permits us to use 220.55. Note 4. allows us to use the table for a branch-circuit for one range. That might stop it right there, as your proposed circuit is more than one range.
The OP said a range, and no nameplate info was given. T220.54 requires us to use Column C, unless permitted in Note 3. That may stop you again.
But lets say you can find a range that is rated only 2500 W. It would need to come with a 30 amp plug on it to work with 210.21(B)(3). That is not what we think of when somone says "a range", and an everyday "range receptacle" won't work here, it would have to be a second "dryer receptacle".
I don't let anyone tell me what type of work I'm going to be responsibile for. The code is a minimum safety standard and this would be safe but it's a darn poor circuit design.
Believe me the customer is not going to accept responsibility for the crappy work, they are going to tell all the neighbors about the breaker that keeps tripping and the electrician that installed it.
No, it has an outlet for one range and an outlet for one dryer.No, the circuit I propose has only one range.
Yes, it does. And if that is what we have that is one thing. But if a person says "a range", they are not automatically planning to order a small custom range.Note 3 says for over 1-3/4kW thru 8-3/4kW, IN LIEU of Column C you can use column A or column B as described. 2.5kW falls into this range of values.
I agree. If it all works, that is fine. I have no moral judgement in this discussion. This is an NEC forum thread, either it can meet code, or it can't.For all I know, this mystery 2500W range would come with a 30A plug on it. Nowhere does the code say a range must be plugged into an "everyday range receptacle." Maybe the range could be hardwired, if it was in sight of the panel, so that the branch c/b served as the disconnecting means. Just because the word "range" is used, that doesn't automatically mean 40A branch circuit and everyday "range receptacle."
No, it has an outlet for one range and an outlet for one dryer.
Yes, it does. And if that is what we have that is one thing. But if a person says "a range", they are not automatically planning to order a small custom range.
I agree. If it all works, that is fine. I have no moral judgement in this discussion. This is an NEC forum thread, either it can meet code, or it can't.
But from the information provided in the OP, what was proposed, interpreted using reasonable assumptions, would meet neither the intent nor the letter of the NEC, IMO.
Using other assumptions, anything is possible.
I always thought it would be a great idea to setup a range and dryer with switch in the front for triggering a contacter... you know for use on the same circuit... you go to one dryer *contacter switches... go to the other dryer... conter switches... so essentially only one dryer would ever be on at once...
...but maybe that's just crazy, but could that work?
mxslick, you're assuming that the range is large enough to cause the breaker to trip, which hasn't been determined from the OP.
P.S. How was the renaissance fair?
What would be "poor" circuit design about adding load to an existing circuit, if that added load does not exceed the circuit rating?
The work would only be "crappy" if you installed it crappily. Why would the breaker be tripping if the load doesn't exceed the circuit rating?
Look at 210.23. Stop making assumptions and read the code. Remember that the code is only concerned with safety - not convenience, adequacy, or even cost. Tripping a circuit breaker is not considered a safety issue.
No, an additional 5760 watts are not ok, the total load shall not exceed the rating of the branch-circuit. 220.18.The question is, can this installation be code compliant. The answer is maybe, but we need more information. 210.23 (B) says that a 30-amp branch circuit may be used for cord and plug connected utilization equipment as long as it does not load the circuit to more than 80% of it's capacity. 30 amps times 240 volts = 7200 watts. 80% of 7200 watts is 5760 watts. Assuming that the dryer is the standard 5000 watt unit, it is OK. If the new range does not calculate to more than 5760 watts (see note 4 to table 220.55 - nameplate could be 7200 watts) the range would be OK.
I agree, but 5760 watts is not a result of careful sizing.Also see table 210.24 - since this is now a multioutlet branch circuit the range receptacle would be required to be 30 amp not 50-amp. The fact that the breaker would trip if both appliances are used simultaneously does not appear to be a code issue, but rather a design issue; so if the homeowner is willing to make that sacrifice to save money, it is their choice. Also remember that if the range that they purchase off of "Craig's list" is rated 8.75 kw or more then a 40-amp circuit IS REQUIRED - see 220.19(3). Bottom line, if you carefully size the new range, it is possible.
Perhaps a gas range should be suggested.
Tripping a circuit breaker is not considered a safety issue.
Sure it is, otherwise we would not need any load calculations.
If it is a safety concern why can I place multiple receptacles on a circuit?