is what i am writing below the same thing as what is found in this old post?
i was in a home that has a 15amp double pole ocpd with one leg going to a 120v recept(neutral present on recept). that leg continues on to one leg of a 240v pump. the other leg of the double ocpd goes straight to the pump. the pump is bonded by being attached to the water pipe.
could someone please reference what the nec says about this? (210-4(c) Exception #2?)
i think this is shoddy work but not really a problem since it is only a 15 amp breaker, right?
thank you,
ron g.
is what i am writing below the same thing as what is found in this old post?
i was in a home that has a 15amp double pole ocpd with one leg going to a 120v recept(neutral present on recept). that leg continues on to one leg of a 240v pump. the other leg of the double ocpd goes straight to the pump. the pump is bonded by being attached to the water pipe.
could someone please reference what the nec says about this? (210-4(c) Exception #2?)
i think this is shoddy work but not really a problem since it is only a 15 amp breaker, right?