Re: dual voltage from ocpd,referencing an old post.
By Steve: The NEC allows branch circuits and multiwire branch circuits.
What we are talking about is neither.
The NEC doesn't say anynthing MULTI CIRCUIT BRANCH WIRES. That's what you guys are talking about with multiple circuits sharing a phase conductor
Now Steve for the purpose of the NEC A multiwire branch circuit has been given a definition:
Branch Circuit, Multiwire. A branch circuit that consists of two or more ungrounded conductors that have a voltage between them, and a grounded conductor that has equal voltage between it and each ungrounded conductor of the circuit and that is connected to the neutral or grounded conductor of the system.
This clearly states that a multi wire circuit is simply a circuit consisting of two hots and a neutral. The two hots have voltage between them, and the neutral has equal voltage between it and each hot.
So any branch circuit that has two hots and a neutral is a multiwire branch circuit!
It does not say anything about any loads it serves or what the voltage of the load is.
A dual voltage receptacle that has two hots on different legs in the panel (voltage between them) and a neutral (equal voltage to each hot) is being fed by a multiwire branch circuit period!
Now 210.4(C) states:
(C) Line-to-Neutral Loads. Multiwire branch circuits shall supply only line-to-neutral loads.
so if each circuit of a multiwire circuit is fed from a single pole breaker then we can only supply line to neutral loads.
But:
Exception No. 1: A multiwire branch circuit that supplies only one utilization equipment.
This allows us to use the multiwire circuit with line to line loads to feed one piece of equipment
Exception No. 2: Where all ungrounded conductors of the multiwire branch circuit are opened simultaneously by the branch-circuit overcurrent device .
Now if we feed both circuits from a two-pole breaker we can also feed line to line loads at the same time.
An exception to a rule is a permission to a rule to allow something that was not allowed. But requirement's within an exception is a requirement that safely allows us to deviate from a requirement.
Allowing line to line loads would be dangerous as you have stated because of voltage feedback through the 240 volt load, A good case of this is when a single fuse blows on leg "B" feeding a trailer home and the electric water heater passes voltage from leg "A" through the element to loads on leg "B" But the requirement in the exception to 210.4(C) only allows this installation if both legs (A&B) are both disconnected in the event of a overload or short. With both legs being disconnected there is no danger anymore. This is why it is allowed as long as you do what the exception Say's in this case "protect both legs with a two-pole breaker rated for the load.
I hope this will open your mind up as we are all here to learn. I have learned many things that I would have made large bets that I was right. I have also learned that the more I stay open minded the more I can learn.
Threads like this has been my biggest learning tool as it makes me dig deeper to find the truth and I have been wrong many times I'm just human.