Re: dual voltage from ocpd,referencing an old post.
OK, I am back. And I am so GLAD that these last few pages have been at my expense, Rong111.
240.20(B)(1) Except where LIMITED by 210.4, individual 1p breakers, with or without identified handle ties, shall be permitted as the protection of each ungrounded conductor of a multiwire branch circuits that serve ONLY single phase LINE TO NEUTRAL loads
240.20 (B)(3) for Line to Line loads in a 4WIRE 3PHASE SYSTEM.... individual single pole breakers WITH identified handles shall be permitted..
210.4(B)Multiwire Branch circuits and 210.7(B) multiple branch circuits that supply devices on the same yoke, a means to simultaneously disconnect the ungrounded conductors shall be provided...
210.4 (C) Line to neuutral loads only
exception (1)... that supplies only one piece of equipment (ie. dryer, range)
exception (2) Where all ungrounded conductors of a mwb circuit are opened simultaneously by the branch circuit overcurrent DEVICE.
In conclusion, I concede that a branch circuit that has 2 ungrounded conductors and a grounded conductor, but feeds a 240v load and a 120v load is legal.
However, there are limitations: exception (2) states that the OCP must be a device, not 2 seperate breakers that are handle tied together. 240.20(B)(1)and(3) also limit us to where and when we can use handleties with single pole breakers, and neither state that we can use 2 single pole breakers, handle tied, for 240 volt loads on a single phase system. 210.4(B) tells us when we need handle ties, for same yoke installations.
Again, I concede that I was originally wrong. Yet, I was not the only one. I would still be careful, because this installation has limitations.
I am still keeping workmanlike manner in my back pocket, because anyone that does this should have real reasons, COST to the contractor and poor PLANNING by contractor are not real reasons. Rong111, costs should not be a factor as you see it in this instance. If the customer doesn't want to pay for proper installation, then don't do it. If the contractor forgot something and is trying to save his/her costs, then it is NOT workmanlike manner.